Bus Heavy with some devices switched off

Post by aranlogic » Fri 25. Mar 2011, 10:58

I have a can-bus network with 8 devices on it. Some times 6 of the devices are powered off. During this the can bus status shows busy heavy. Using an oscilloscope I can see corruption of the CAN Hi and Lo signals. I loose communication ability to the 2 devices which are not switched off.

Is it possible to use the PCAN-Repeater to isolate the bus devices which are switched off from the ones that are not?

M.Maidhof
Support
Support
Posts: 1675
Joined: Wed 22. Sep 2010, 14:00

Re: Bus Heavy with some devices switched off

Post by M.Maidhof » Mon 28. Mar 2011, 11:38

Hi,

thanks for the info. Unfortunately a PCAN-Repeater will not help in that configuration, because it looks like those devices which are powered off will disturb the physical CAN layer, so the repaeter will tranfers those bad signals also from one to the other side.
A solution will be a PCAN-Router, which will not transfer bad signals from one to the other side, because there are 2 CAN-Controller inside.

best regards

Michael

aranlogic
Posts: 2
Joined: Fri 25. Mar 2011, 10:52

Re: Bus Heavy with some devices switched off

Post by aranlogic » Thu 31. Mar 2011, 13:06

I tried both the PCAN-Repeater and the PCAN-Router.

The PCAN-Repeater fails as you suggested.
The PCAN-Router works first time staight out of the box :)

Many thanks

User avatar
U.Wilhelm
Sales & Support
Sales & Support
Posts: 1636
Joined: Fri 10. Sep 2010, 19:34

Re: Bus Heavy with some devices switched off

Post by U.Wilhelm » Mon 26. Sep 2016, 08:43

closed
--------------------------------