Hi,
I'm using PCAN-USB between PC and microcontroller for continuously collecting data from microcontroller to PC. Data transfer is happening successfully but when 20 minutes are elapsed the PCAN stops receiving the data (the data from the microcontroller is still being sent on the bus).
what could be the possible reason of abrupt malfunctioning at 20 minutes?
Data receiving is getting stopped
Re: Data receiving is getting stopped
Hi,
please provide details about used OS, driver version and software which displays the data.
regards
Michael
please provide details about used OS, driver version and software which displays the data.
regards
Michael
Re: Data receiving is getting stopped
Hi
here are the required details.
1. OS is windows.
2. driver version is PCAN-Basic V4.6.0.600.
3. Software which display data is PCAN-View.
here are the required details.
1. OS is windows.
2. driver version is PCAN-Basic V4.6.0.600.
3. Software which display data is PCAN-View.
Re: Data receiving is getting stopped
Hi,
please check your CAN wiring for correct termination on both ends. Please enable the "log error frames" in the trace option, and log the data in a ring buffer, to see what is happening after 20 minutes. Please also provide details about driver version, PCANBasic is only the API, not the driver.
regards
Michael
please check your CAN wiring for correct termination on both ends. Please enable the "log error frames" in the trace option, and log the data in a ring buffer, to see what is happening after 20 minutes. Please also provide details about driver version, PCANBasic is only the API, not the driver.
regards
Michael
Re: Data receiving is getting stopped
Hi,
the driver used is PCAN_USB 4.3.0.16563.
the driver used is PCAN_USB 4.3.0.16563.
- PEAK-Support
- Sales & Support
- Posts: 1646
- Joined: Fri 10. Sep 2010, 19:34
Re: Data receiving is getting stopped
Driver is up to date - but please answer the other questions.
- Check Termination (MUST be ~60 Ohm between CAN-H and CAN-L when System is powered off)
- Run the Tracer with all Error Flags settings set as Michael told you
- Check Termination (MUST be ~60 Ohm between CAN-H and CAN-L when System is powered off)
- Run the Tracer with all Error Flags settings set as Michael told you
--------------------------------
PEAK-System Technik
Technical Support Team
support[at]peak-system.com
-------------------------------
PEAK-System Technik
Technical Support Team
support[at]peak-system.com
-------------------------------