Strange CAN BUS waveforms when using the PCAN optoadapter
Plug-in Adapter for Decoupling CAN Networks
Nick_Adams
Post by Nick_Adams » Fri 28. May 2021, 12:31
Hi all,
I have 3 devices in a CAN bus system.
1st device is isolated from the others by using the PCAN optoadapter.
CAN BUS data rate is 250kB/sec
1st sends 4 TPDOS at 100ms.
2nd device sends 1 TPDO at 10ms
3rd device sends 4 TPDOs at 100ms.
Cable length 2-3meters.
The 1st device distorts the bus as the following figure shows:
CANH_CANL
CANH_CANL
When I reduce the 1st device TPDOS to 2, then there is no issue on the bus.
Unfortunately I do not have access before the isolation but only after were all devices are connected.
Do you have any hint why this is happening?
Thank you
Nick
Re: Strange CAN BUS waveforms when using the PCAN optoadapter
Post by M.Heidemann » Fri 28. May 2021, 15:38
Please check the termination on your system in an unpowered state, make sure
you have around 60 Ohms between CAN-High and CAN-Low on both sides.
It could be possible that you need additional termination on your primary side.
Please report back to us with your findings.
Marvin.
Nick_Adams
Post by Nick_Adams » Mon 31. May 2021, 17:28
Hi Marvin,
Eventually I was able to replicate the fault that the customer sees in the lab.
The issue is time related because the power supply of the PCAN opto-adapter goes lower than the PCAN opto-adapter threshold and this makes it to complain.
When I reduce the TPDOs then the needed power is lower and the issue goes away.
I will upload some more photos tomorrow.
Thank you
Nick
Post by M.Heidemann » Wed 2. Jun 2021, 12:29
Hello Nick,
Please make sure the PCAN-Optoadaptor is properly supplied with the needed voltage throughout your tests.
Furthermore, did you manage to obtain the aforementioned pictures?
marvin