Posted: Tue 10. Aug 2021, 22:47
by Tesmec
Hello folks, I'm investigating a random issue that affect a j1939 bus. From time to time the bus stop working properly, the bus load reach 95% and a sequence of error frames is broadcasted. Can anyone explain if is possible to get any clue on the issue decodic the error frames? If yes, how could I decode them?
Attached part of a trace where the error frames show up.
Any help is appreciated.
Re: Error frame
Posted: Wed 11. Aug 2021, 08:06
by M.Heidemann
Hello,
You can always refer to the PEAK-Trace format description:
https://www.peak-system.com/produktcd/P ... Format.pdf
In your case, please look up format-version 2.0 (Page 112 of the document), which is used by PCAN-View.
Your trace shows form-errors, which do occur if the CAN-controller detects an invalid value
in of the CAN-Frames expected fields.
There are multiple possible causes for this, please check the following:
- Does the used bitrate match on all devices on the bus? (Also check the used sample-point)
- Is you CAN-Bus properly terminated? (120 Ohm on both bus ends, you should have ~60 Ohms between CAN-high and CAN-Low on the bus in an unpowered state)
- Check your cabling for possible damages
Please report back to us with your findings.
Best Regards
Marvin
Re: Error frame
Posted: Wed 11. Aug 2021, 14:22
by Tesmec
Hello Marvin,
thanks for the quick response.
After several hours of investigation we did find the cause, it was a connection for a spare node, apparently well realized and properly capped, full of mud and moisture.
In certain conditions, not continuosly, the bus was reaching 95% load and voltage CANH-GND a value of 6.5V.
Hope this experience will help other people in their troubleshooting activities.
Regards.