Send ini table for slaves
Posted: Fri 3. Feb 2023, 14:33
Hello,
before using the standard schedule table to control the slaves I need to initialize all of them by sending this procedure:
Schedule_tables {
sch_mreq {
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0xFF, 0xFF, 0xFE } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x1, 0xF1, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x19 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x18 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x17 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x16 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x15 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x14 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x13 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x12 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x11 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x10 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xE } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xD } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xC } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xB } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xA } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x9 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x8 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x7 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x6 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x5 } delay 10 ms ;
SlaveResp delay 100 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x4 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x19, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x18, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x17, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x16, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x15, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x14, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x13, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x12, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x11, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x10, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xF, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xE, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xD, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xC, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xB, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xA, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x9, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x8, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x6, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x5, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x4, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x3, 0xF1, 0xFF } delay 10 ms ;
SlaveResp delay 1000 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x4, 0xF1, 0xFF } delay 10 ms ;
SlaveResp delay 1000 ms ;
FreeFormat { 0x19, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x19, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x99 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x18, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x18, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xD8 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x17, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x17, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x97 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x16, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x16, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xD6 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x15, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x15, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x55 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x14, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x14, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x14 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x13, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x13, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xD3 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x12, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x12, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x92 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x11, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x11, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x11 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x10, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x10, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x50 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xF, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xF, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xCF } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xE, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xE, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x8E } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xD, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xD, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xD } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xC, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xC, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x4C } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xB, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xB, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x8B } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xA, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xA, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xCA } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x9, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x9, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x49 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x8, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x8, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x8 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x7, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x47 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x6, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x6, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x6 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x5, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x5, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x85 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x4, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x4, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xC4 } delay 300 ms ;
SlaveResp delay 200 ms ;
}
Can anybody tell me whats the best way to do that? In PLIN View Pro or Ipemotion?
thanks in advance!
br
Michael
before using the standard schedule table to control the slaves I need to initialize all of them by sending this procedure:
Schedule_tables {
sch_mreq {
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0xFF, 0xFF, 0xFE } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x1, 0xF1, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x19 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x18 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x17 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x16 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x15 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x14 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x13 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x12 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x11 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x10 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xE } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xD } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xC } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xB } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0xA } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x9 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x8 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x7 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x6 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x5 } delay 10 ms ;
SlaveResp delay 100 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x2, 0xF1, 0x4 } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x19, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x18, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x17, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x16, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x15, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x14, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x13, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x12, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x11, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x10, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xF, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xE, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xD, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xC, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xB, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xA, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x9, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x8, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x6, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x5, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x4, 0x6, 0xB2, 0x0, 0xFF, 0x7F, 0xFF, 0xFF } delay 10 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x3, 0xF1, 0xFF } delay 10 ms ;
SlaveResp delay 1000 ms ;
FreeFormat { 0x7F, 0x6, 0xB5, 0xFF, 0x7F, 0x4, 0xF1, 0xFF } delay 10 ms ;
SlaveResp delay 1000 ms ;
FreeFormat { 0x19, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x19, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x99 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x18, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x18, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xD8 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x17, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x17, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x97 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x16, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x16, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xD6 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x15, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x15, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x55 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x14, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x14, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x14 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x13, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x13, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xD3 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x12, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x12, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x92 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x11, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x11, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x11 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x10, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x10, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x50 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xF, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xF, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xCF } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xE, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xE, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x8E } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xD, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xD, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xD } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xC, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xC, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x4C } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xB, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xB, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x8B } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0xA, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0xA, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xCA } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x9, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x9, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x49 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x8, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x8, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x8 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x7, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x7, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x47 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x6, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x6, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x6 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x5, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x5, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0x85 } delay 300 ms ;
SlaveResp delay 200 ms ;
FreeFormat { 0x4, 0x6, 0xB1, 0xFF, 0x7F, 0x1, 0x0, 0xE2 } delay 300 ms ;
FreeFormat { 0x4, 0x6, 0xB1, 0xFF, 0x7F, 0x2, 0x0, 0xC4 } delay 300 ms ;
SlaveResp delay 200 ms ;
}
Can anybody tell me whats the best way to do that? In PLIN View Pro or Ipemotion?
thanks in advance!
br
Michael