Hello!
Trying to read the DIN0 with the PCAN-Router FD with the following code.
// variable for storing Digital Input
uint32_t diStatus = 0;
In int main function
// check digital input and send out status on CAN
HW_GetDIN ( &diStatus );
din0 = (diStatus >> 0) & 1;
This always gives me a zero on the input even though I measure 0 and 12 V on the pin 8 of the CAN2 D-sub.
Two questions, is pin 8 the correct input of DIN0 and is also necessary to have power on pin 9 and GND on Pin 3 on CAN2 input to be able to read the DIN0 input pin?
Regards Emil
Reading DIN0
Re: Reading DIN0
If i am not completely mistaken you are assigning DinStatus which you set to 0 to Din0,
then you would come up 0 every time regardless of what the input actually reads...
Am i misunderstanding what you are doing here?
BR
BR
Re: Reading DIN0
Hi!
Have had winter holidays now back to this problem.
I'm assigning diStatus to zero at initialization, then in the while loop HW_GetDIN is called and address of diStatus is sent as an argument to the HW_GetDIN function.
This to me should give me the current status of DIN into the value of variable diStatus.
Then din0 is given status of bit 0 of diStatus that should be status of DIN0. But this is always 0.
If I do not perform the bit-wise check on diStatus it is read as decimal 6 but it never changes if I switch the switch on DIN0 input.
Can you confirm that DIN0 input pin is PIN8 in the DSUB 2 on the PCAN-Router FD.
And I used a 10 kohm resistor between pin 9 and pin 8 and the switch is between pin 9 and pin 3.
Is this setup correct?
Regards Emil
Regards Emil
Re: Reading DIN0
Solved
The cabling was the problem, it was always tied to ground. After fixing cabling then works as intended.
//Emil
//Emil
Re: Reading DIN0
Hello Emil,
Thank you for letting us know!
BR
marvin
BR
marvin