Hi,
I would like to trigger two LED's connected to the AOut 0 and AOut1 depending on the
state of the same 1-bit signal on CAN.
I'm only able to turn either ON when the bit value is = "1" but not when it's "0".
Would it be possible to create the following logic in PCAN MicroMod for Analog2?
Bit Value AOut1 AOut2
0 ON OFF
1 OFF ON
If this can only be done using custom firmware could someone please provide and example code on how
this could be done?
Thanks
Analog Out enabled on bit 0 value for Analog2
Re: Analog Out enabled on bit 0 value for Analog2
Hello,
please look at the attached example:
AOUT 0 is controlled via CAN-ID 0x100, Byte0, Bit 0. Scale is set to -4000, Offset is set to 4000.
If the bit is 0:
(0* -4000) + 4000 = 4000 (led goes on)
if the bit is 1:
(1* -4000) + 4000=0 (led goes off)
AOUT 1 is also controlled via CAN-ID 0x100, Byte0, Bit 0. Scale is set to 4000, Offset is set to 0.
If bit is 0:
(0* 4000) + 0 = 0 (led goes off)
If bit is 1
(1* 4000) + 0 = 4000 (led goes on)
A value of 4000 represents ~9.75V.
Regards,
Gunnar Bohlen
please look at the attached example:
AOUT 0 is controlled via CAN-ID 0x100, Byte0, Bit 0. Scale is set to -4000, Offset is set to 4000.
If the bit is 0:
(0* -4000) + 4000 = 4000 (led goes on)
if the bit is 1:
(1* -4000) + 4000=0 (led goes off)
AOUT 1 is also controlled via CAN-ID 0x100, Byte0, Bit 0. Scale is set to 4000, Offset is set to 0.
If bit is 0:
(0* 4000) + 0 = 0 (led goes off)
If bit is 1
(1* 4000) + 0 = 4000 (led goes on)
A value of 4000 represents ~9.75V.
Regards,
Gunnar Bohlen
- Attachments
-
- AO0_AO1_1bit.mcf
- (1.69 KiB) Downloaded 2158 times
Re: Analog Out enabled on bit 0 value for Analog2
Hi Gunnar,
Thank you very much for the input. This was exactly what I wanted to have.
Is there by any chance also the possibility of having the output run with a frequency
output or is this only available on other hardware models?
Thanks
Thank you very much for the input. This was exactly what I wanted to have.
Is there by any chance also the possibility of having the output run with a frequency
output or is this only available on other hardware models?
Thanks
Re: Analog Out enabled on bit 0 value for Analog2
Hello,
the Analog2 MicroMod don´t have frequency outputs. Only the Digital1/2 and Mix MicroMod modules offers frequency outputs. Please see product info on our website for more details.
regards
Michael
the Analog2 MicroMod don´t have frequency outputs. Only the Digital1/2 and Mix MicroMod modules offers frequency outputs. Please see product info on our website for more details.
regards
Michael