Bus-off on any sending attempt - PCAN - USB
USB to CAN Interface
MarcinSzn
Post by MarcinSzn » Wed 1. Sep 2021, 13:32
For a few days I am facing problem with PCAN - USB.
I am using Can network with bitrate of 500 kBit/s and extended IDs.
On any transmit attempt (tried with different Can networks) Peak goes into Bus-OFF state. Moreover Peak is no acknowledging any other Can messages although option "Listen-Only Mode" being turned off. Here is status of the bus when transmission attempt occurs:
Zrzut ekranu 2021-09-01 132605.png (26.42 KiB) Viewed 6857 times
And registered by another CAN device:
Zrzut ekranu 2021-09-01 132844.png (8.56 KiB) Viewed 6857 times
Before sending attempt PeakUSB is receiving CAN messages correctly.
The attempted message is not sent to CAN network.
I would be very grateful for any help
Re: Bus-off on any sending attempt - PCAN - USB
Post by M.Heidemann » Wed 1. Sep 2021, 13:48
Check the following:
Is your bus properly terminated (120 Ohms on both bus ends)?
Does your bitrate match? (Also check the sampel-Point)
Check for duplicate messages, if the two identical IDs collide they
also could cause this behavior.
Check your cabling, is it correct? Ar there any defects?
Please share your findings with us
MarcinSzn
Post by MarcinSzn » Wed 1. Sep 2021, 14:24
Yes, I've also tried with no, or single termination with no difference.
Yes, 3 devices have 500 kBit/s with sampling point of 87,5%. 2 devices can communicate with each other with no problem. Peak can read whole communication, but is causing error with sending attempt.
Also Peak is having exactly the same errors when is the only device on bus network.
Check for duplicate messages, if the two identical IDs collide they also could cause this behavior.
Every device is sending messages with different IDs
Unfortunately I couldn't find any problem with cabling. It is a test network with overall length less than 1m
Post by M.Heidemann » Wed 1. Sep 2021, 14:47
Heello,
Thank you for your fast reply.
We suspect this still comes down to the bitrate settings.
We assume you use PCAN-View?
Please try a Btr0Btr1 of "0x4114h" as a test:
Additionally you could check if your device has an defective transceiver:
viewtopic.php?f=120&t=52
MarcinSzn
Post by MarcinSzn » Thu 2. Sep 2021, 07:38
Thank you for answer.
It looks like trans-receiver is defective because:
4. Please measure with a multimeter (DC measurement area) the voltage the between pin 2 (CAN-L) and pin 3 (GND) from the 9 pole D-SUB. You should measure 2.5V +/- 0.2V
Voltage is: 4.21
5. Now measure the voltage between pin 7 (CAN-H) and pin 3 (GND) from the 9 pole D-SUB, you should also measure 2.5V +/- 0.2V
Voltage is: 1.54
Thank you for support!
Post by M.Heidemann » Thu 2. Sep 2021, 15:50
Dear Marcin,
Did you measure these values while idle?
Please let us know
MarcinSzn
Post by MarcinSzn » Thu 9. Sep 2021, 07:30
Sorry for the slow response. Yes I've measured above values on idle (nothing connected to PeakCAN, RED LED light on, not blinking)
When device is connected (RED LED blinking) values are essentially the same
Post by M.Heidemann » Thu 9. Sep 2021, 10:06
Thanks for the info,
just wanted to make sure this also
was mesaured in idle.
Sounds like either a Transceiver defect or a defective opto-decoupler (If you device is a IPEH-002022)